About 600 results
Open links in new tab
  1. Open Vs Closed Circuit Cooling Towers | Eng-Tips

    Jun 27, 2007 · After doing a little research I came across various closed circuit cooling towers, and I was wondering if anyone has had experience switching from an older open circuit …

  2. autotransformer open circuit vs closed circuit | Eng-Tips

    Dec 20, 2004 · Here is a link that shows a diagramatic comparison of the open transition and the Korndorfer closed transition type. For the closed transition they use a manually operated …

  3. Star-Delta Starter: Open or Closed Transition? | Eng-Tips

    Apr 3, 2006 · As a rule, even the heavier duty solid state starters are going to cost the same or less than a closed transition Y-D starter now. The move up from Open to Closed transition …

  4. Open versus Closed Transitioning on Medium Voltage Switches

    May 4, 2009 · In my research on open versus closed transition switching, I fount this: Open Transition Transfer Switches An open transfer switch’s connection with a generator is …

  5. How to calculate NPSHA in a closed pumping Loop? | Eng-Tips

    Oct 12, 2007 · Right, anywhere in the loop. In a closed circuit, sum of heads lost = pump head + initial head. You have to maintain a minimum (initial) head/pressure in the loop, such that you …

  6. Substation Trip versus Open nomenclature | Eng-Tips

    Jun 11, 2009 · Look at all of the photos and diagrams of breaker control switches in the Electroswitch catalog. I would say Trip for any operation that energizes a "Trip" coil to open a …

  7. Who determined to use green for open and red for closed in

    Mar 22, 2007 · The front of this supervisory controller was full of indicator lights for each station switch position: red=closed, green=open, white=Automatic (tripping) operation, and amber for …

  8. Soft Load & Open/Closed Transition | Eng-Tips

    Nov 17, 2008 · Open transition = break before make. Closed transition = make before break. If you are looking at closed transition switching using breakers that tie a utility circuit to any …

  9. wye delta closed transition starting | Eng-Tips

    Aug 12, 2002 · The wye-delta starter is available in both open and closed transition configurations. Closed transition starters are supplied with an additional contactor and resistor …

  10. Fail safe vs Non fail safe | Eng-Tips

    Mar 10, 2004 · Fail-safe or Not Fail-safe, is purely to do with how the rest of the circuit is wired. If a breaker requires a closure to trip, then the "fail-safe" mode would be normally closed, …